NEW OR REWIRED DOMESTIC AND SIMILAR INSTALLATIONS

 

NDQ1

Does the 17th Edition require all 13 A socket-outlets in domestic premises need to be RCD-protected?

 

NDA1

For new installations and rewires in domestic premises, all socket-outlets need to have additional protection by RCD, except perhaps for those intended to supply particular items of equipment such as freezers. Any socket-outlet not having RCD protection needs to be specifically labelled or otherwise suitably identified to indicate its intended use, such as ‘freezer only’.

 

411.3.3

NDQ2

The 17th Edition requires most if not all circuits in domestic premises to be RCD-protected. There have been a number of suggestions as to how the consumer unit may best be configured to comply with the Regulations, the most common being a main switch with RCBOs protecting each individual circuit. However, another suggestion favours a main switch with two RCDs protecting separate DIN rails. If careful consideration is given as to what each bar will control in the way of upstairs and downstairs lighting and power circuits, will this configuration comply?

 

NDA2

Yes, as long as the division of final circuits between the RCDs is carefully considered so as to minimize the consequences of unwanted tripping. Separate RCD protection is not necessarily required for each circuit of an installation but, in order to minimize the consequences of tripping, a single (‘front end’) RCD should not be used to protect all the circuits.

 

314.1

NDQ3

The 17th Edition does not now define a zone 3 in a bathroom or shower room. What electrical equipment and accessories can be installed in the area between 0.6 m and 3.0 m from the edge of the bath or shower basin? Moreover, what minimum degree of IP protection are manufacturers likely to recommend?

 

NDA3

There is no change from the 16th Edition requirements – that is, the general rules apply.  The manufacturer’s installation instructions must always be followed.

 

512.2
134.1.1

 

NDQ4

Do ‘meter tails’ concealed in walls or partitions need to be protected in accordance with Regulations 522.6.6 and/or 522.6.8?

 

NDA4

Yes. Meter tails concealed in a wall or partition at a depth of less than 50 mm from a surface must be protected in accordance with Regulation 522.6.6. Also, irrespective of the depth from a surface, meter tails concealed in a wall or partition having internal metallic parts (except nails and screws, etc) are subject to the requirements of Regulation 522.6.8.

However, additional protection for meter tails by means of an RCD is not an acceptable option in respect of Regulation 522.6.7 (which in consequence rules out reliance on 522.6.6(v), routing in the ‘safe zones’ alone), or in respect of Regulation 522.6.8(v). Also, for TT systems, the only option remaining is to provide suitable mechanical protection (that is, to comply with Regulations 522.6.8(iv) and/or 522.6.6(iv) as appropriate).

 

522.6.6, 522.6.8
314.1, 314.2

NDQ5

Where the Regulations specify additional protection by RCD, does this include RCBOs?

 

NDA5

Yes. Where the generic term ‘RCD’ is used, it refers to most types of residual current device including RCBOs (Residual current-operated circuit-breakers with integral overcurrent protection), RCCBs (Residual current-operated circuit-breakers without integral overcurrent protection) and SRCDs (Socket-outlets incorporating a residual current device). For the purposes of the Regulations, it does not include PRCDs (Portable residual current devices).

 

411.3.3

NDQ6

Does boiler pipework need to have additional equipotential bonding for electrical safety reasons?

 

NDA6

There is no specific requirement in the Regulations for boiler pipework to be supplementary bonded. However, such bonding may be called for in the boiler manufacturer’s instructions, in which case BS 7671 requires those instructions to be followed (Regulation 510.2 refers). Any stated requirement for additional bonding that is considered to be unnecessary should be queried with the manufacturer concerned, and amended installation instructions requested.

 

411.3.3

NDQ7

Does the dispensation in Regulation 701.415.2 to omit supplementary bonding in a location containing a bath or shower apply to TT systems?

 

NDA7

Yes

 

701.415.2

NDQ8

If the mains supply cable to a fixed appliance such as a flat screen TV is concealed in a wall or partition at a depth of less than 50 mm, does the 17th Edition require the lead to be RCD-protected in accordance with Regulation 522.6.7 even though it’s connected by means of a plug and socket?

 

NDA8

Yes. The risk of penetration by a nail or screw is the same as for other concealed cable. Also, if the wall or partition has internal metallic parts (except nails and screws, etc), RCD protection in accordance with Regulation 522.6.8 is required irrespective of the depth of the cable from the surfaces.

 

522.6.7, 522.6.8

NDQ9

To overcome thermal insulation issues, is it permissible to design a ring final circuit using 2.5 mm2 cable protected by a 20 A protective device?

 

NDA9

Yes, if the effective current carrying capacity of the cable is at least 12.5 A (20 A × 20/32), so as to effectively have the same ‘deemed to comply status’ as Regulation 433.1.5 gives to 30 A and 32 A ring final circuits.

 

433.1.5

NDQ10

Should signal amplifiers mounted at high level on television aerials where they might be struck by lightning be main bonded?

 

NDA10

There is no specific requirement in BS 7671 but, if there is considered to be a significant risk of a lightning strike, the advice of a lightning protection specialist should be sought.

 

 

NDQ11

I am working on a new electrical installation which was designed to the 16th Edition but which will not be completed until after the 17th Edition comes into full effect. To which Edition should the installation be inspected, tested, verified and certificated?

 

NDA11

An installation designed and installed to the 16th Edition should be inspected, tested, verified and certificated to that Edition.

 

 

NDQ12

What types of mechanical protection provide sufficient protection against penetration by nails, screws and the like?

 

NDA12

As an example, steel of 3 mm minimum thickness is generally considered to provide sufficient mechanical protection, except where shot-fired nails are likely to be used.

 

 

522.6.6
522.6.8

 

NDQ13

Five flats are fed individually from five ‘sub-mains’ originating at the main intake position. The five gas and water meters are main bonded at the main intake position. Do we still need to provide main bonding in each of the flats?

 

NDA13

Whilst main protective bonding is required at the main intake position, it is good practice also to provide main protective bonding in each flat even though, in this case, the origin of each installation could be considered to be at the main intake position.

 

411.3.1.2

NDQ14

Is an RCD main switch (such as a 100 mA time-delayed device) still required in the consumer unit of a new domestic installation forming part of a TT system?

 

NDA14

For a domestic installation complying with the 17th Edition where all the final circuits are RCD-protected, an RCD main switch is no longer required.

 

 

 


 
The Electrical Safety Council and other members of the forum believe that the guidance and information contained in this section of the website is correct, but all parties must rely on their own skill and judgement when making use of it. Neither the Electrical Safety Council nor any of the other members of the forum assumes any liability to anyone for any loss or damage caused by any error or omission in this section of the website, whether such error or omission is the result of negligence or any other cause. Where reference is made to legislation, it is not to be considered as legal advice. Any and all such liability is disclaimed.

Note: Unless otherwise indicated, all references to ‘RCD’ in this section relate to residual current devices having a rated residual operating current (IΔn ) not exceeding 30 mA and an operating time not exceeding 40 ms at a residual operating current of 5 IΔn  provided as additional protection in the event of failure of the provision for basic protection and/or the provision for fault protection or carelessness by users (Regulation 415.1.1)

 

..............................................................................................................................................................................