ND |
NEW OR REWIRED DOMESTIC AND SIMILAR INSTALLATIONS |
|
|
NDQ1
|
Does the 17th Edition require all 13 A socket-outlets in domestic premises need to be RCD-protected? |
|
|
NDA1
|
For new installations and rewires in domestic premises, all socket-outlets need to have additional protection by RCD, except perhaps for those intended to supply particular items of equipment such as freezers. Any socket-outlet not having RCD protection needs to be specifically labelled or otherwise suitably identified to indicate its intended use, such as ‘freezer only’.
|
411.3.3
|
|
NDQ2
|
The 17th Edition requires most if not all circuits in domestic premises to be RCD-protected. There have been a number of suggestions as to how the consumer unit may best be configured to comply with the Regulations, the most common being a main switch with RCBOs protecting each individual circuit. However, another suggestion favours a main switch with two RCDs protecting separate DIN rails. If careful consideration is given as to what each bar will control in the way of upstairs and downstairs lighting and power circuits, will this configuration comply? |
|
|
NDA2
|
Yes, as long as the division of final circuits between the RCDs is carefully considered so as to minimize the consequences of unwanted tripping. Separate RCD protection is not necessarily required for each circuit of an installation but, in order to minimize the consequences of tripping, a single (‘front end’) RCD should not be used to protect all the circuits.
|
314.1
|
|
NDQ3
|
The 17th Edition does not now define a zone 3 in a bathroom or shower room. What electrical equipment and accessories can be installed in the area between 0.6 m and 3.0 m from the edge of the bath or shower basin? Moreover, what minimum degree of IP protection are manufacturers likely to recommend? |
|
|
NDA3
|
There is no change from the 16th Edition requirements – that is, the general rules apply. The manufacturer’s installation instructions must always be followed.
|
512.2
134.1.1
|
|
NDQ4
|
Do ‘meter tails’ concealed in walls or partitions need to be protected in accordance with Regulations 522.6.6 and/or 522.6.8? |
|
|
NDA4
|
Yes. Meter tails concealed in a wall or partition at a depth of less than 50 mm from a surface must be protected in accordance with Regulation 522.6.6. Also, irrespective of the depth from a surface, meter tails concealed in a wall or partition having internal metallic parts (except nails and screws, etc) are subject to the requirements of Regulation 522.6.8.
However, additional protection for meter tails by means of an RCD is not an acceptable option in respect of Regulation 522.6.7 (which in consequence rules out reliance on 522.6.6(v), routing in the ‘safe zones’ alone), or in respect of Regulation 522.6.8(v). Also, for TT systems, the only option remaining is to provide suitable mechanical protection (that is, to comply with Regulations 522.6.8(iv) and/or 522.6.6(iv) as appropriate).
|
522.6.6, 522.6.8
314.1, 314.2
|
|
NDQ5
|
Where the Regulations specify additional protection by RCD, does this include RCBOs? |
|
|
NDA5
|
Yes. Where the generic term ‘RCD’ is used, it refers to most types of residual current device including RCBOs (Residual current-operated circuit-breakers with integral overcurrent protection), RCCBs (Residual current-operated circuit-breakers without integral overcurrent protection) and SRCDs (Socket-outlets incorporating a residual current device). For the purposes of the Regulations, it does not include PRCDs (Portable residual current devices).
|
411.3.3
|
|
NDQ6
|
Does boiler pipework need to have additional equipotential bonding for electrical safety reasons? |
|
|
NDA6
|
There is no specific requirement in the Regulations for boiler pipework to be supplementary bonded. However, such bonding may be called for in the boiler manufacturer’s instructions, in which case BS 7671 requires those instructions to be followed (Regulation 510.2 refers). Any stated requirement for additional bonding that is considered to be unnecessary should be queried with the manufacturer concerned, and amended installation instructions requested.
|
411.3.3
|
|
NDQ7
|
Does the dispensation in Regulation 701.415.2 to omit supplementary bonding in a location containing a bath or shower apply to TT systems? |
|
|
NDA7
|
Yes
|
701.415.2
|
|
NDQ8
|
If the mains supply cable to a fixed appliance such as a flat screen TV is concealed in a wall or partition at a depth of less than 50 mm, does the 17th Edition require the lead to be RCD-protected in accordance with Regulation 522.6.7 even though it’s connected by means of a plug and socket? |
|
|
NDA8
|
Yes. The risk of penetration by a nail or screw is the same as for other concealed cable. Also, if the wall or partition has internal metallic parts (except nails and screws, etc), RCD protection in accordance with Regulation 522.6.8 is required irrespective of the depth of the cable from the surfaces.
|
522.6.7, 522.6.8
|
|
NDQ9
|
To overcome thermal insulation issues, is it permissible to design a ring final circuit using 2.5 mm2 cable protected by a 20 A protective device? |
|
|
NDA9
|
Yes, if the effective current carrying capacity of the cable is at least 12.5 A (20 A × 20/32), so as to effectively have the same ‘deemed to comply status’ as Regulation 433.1.5 gives to 30 A and 32 A ring final circuits.
|
433.1.5
|
|
NDQ10
|
Should signal amplifiers mounted at high level on television aerials where they might be struck by lightning be main bonded? |
|
|
NDA10
|
There is no specific requirement in BS 7671 but, if there is considered to be a significant risk of a lightning strike, the advice of a lightning protection specialist should be sought.
|
|
|
NDQ11
|
I am working on a new electrical installation which was designed to the 16th Edition but which will not be completed until after the 17th Edition comes into full effect. To which Edition should the installation be inspected, tested, verified and certificated? |
|
|
NDA11
|
An installation designed and installed to the 16th Edition should be inspected, tested, verified and certificated to that Edition.
|
|
|
NDQ12
|
What types of mechanical protection provide sufficient protection against penetration by nails, screws and the like? |
|
|
NDA12
|
As an example, steel of 3 mm minimum thickness is generally considered to provide sufficient mechanical protection, except where shot-fired nails are likely to be used.
|
522.6.6
522.6.8
|
|
NDQ13
|
Five flats are fed individually from five ‘sub-mains’ originating at the main intake position. The five gas and water meters are main bonded at the main intake position. Do we still need to provide main bonding in each of the flats? |
|
|
NDA13
|
Whilst main protective bonding is required at the main intake position, it is good practice also to provide main protective bonding in each flat even though, in this case, the origin of each installation could be considered to be at the main intake position.
|
411.3.1.2
|
|
NDQ14
|
Is an RCD main switch (such as a 100 mA time-delayed device) still required in the consumer unit of a new domestic installation forming part of a TT system? |
|
|
NDA14
|
For a domestic installation complying with the 17th Edition where all the final circuits are RCD-protected, an RCD main switch is no longer required.
|
|